User: markschmitter, Location: Iowa
Asked on: Thursday, February 24, 2011 at 8:26 pm EST
Answered on: Tuesday, May 14, 2024 at 2:01 am EDT
Question: I work in a industrial foundry in Iowa. Im having troubles deciding ifwhat ive done is code true. We install a used portable type horizontalbandsaw. Running on 480 Vac. Because of the position they wanted it sittingand everything else involved the Cord which is SOO and 480 vac twistloc plugare a bit on the long side. Around 10feet. What is the correct code andwhere do i find it. I dont have a new 2011 update. Thanks for your time Mark
NEC Code Requirements
The National Electrical Code (NEC) addresses the installation of cords for portable equipment in Article 400.
Section 400.9(A) states that cords for portable equipment shall not exceed the following lengths: 25 feet for cords rated up to 125 volts, unless a listed cord assembly is used 50 feet for cords rated at over 125 volts, unless a listed cord assembly is usedSection 400.9(B) allows for longer cords if the equipment is connected to a permanently installed outlet and the cord is secured to a support system. However, the maximum length is not specified.
Interpretation
Your situation does not meet the requirements of Section 400.9(A) because the cord for the bandsaw exceeds 50 feet. However, Section 400.9(B) may allow for a longer cord if it meets the following conditions: The bandsaw is connected to a permanently installed outlet (e.g., a wall receptacle) The cord is secured to a support system (e.g., hooks or clamps) at regular intervalsRecommendation
To ensure compliance with the NEC, you should: Connect the bandsaw to a permanently installed outlet and secure the cord to a support system at regular intervals. Document the installation and provide a copy to the local electrical inspector for review.
Note:
It is always recommended to use the most recent edition of the NEC for the most up-to-date and accurate information. Flag for review