Question: recently I read aproblem asking to calculate the volt ampre number required to be used in sizing the conductor and overcurrent device for a store 60' by 80' of which 400 sq. was used for storage.the answer they gave was 4400 sq at 3va=13200va plus 400sq at 1/4=100 for a total of 13300va.I would think it should be 13200 x 1.25=16500 plus 100 for a total of 16600va to size the feeder.what do you guys think?
The answer given in the problem is incorrect. The correct total volt-ampere (VA) number for sizing the conductor and overcurrent device for the store should be 16,600 VA, not 13,300 VA.Here is the correct calculation: 4400 sq. ft. at 3 VA/sq. ft. = 13,200 VA 400 sq. ft. at 1/4 VA/sq. ft. = 100 VATotal: 13,200 VA + 100 VA = 13,300 VA* Add 25% for diversity = 13,300 VA x 1.25 = 16,600 VATherefore, the total VA number required to be used in sizing the conductor and overcurrent device for the store is 16,600 VA, not 13,300 VA. Flag for review