Topic: Art. 310 Ambient temp tables 2011

User: wireguy8169, Location: Southern Maine

Asked on: Thursday, February 24, 2011 at 8:56 pm EST
Answered on: Tuesday, May 14, 2024 at 2:01 am EDT

Question: When would you use Table 310.15(B)(2)(a) versus Table 310.15(B)(2)(b). This came up in class this evening and for the life of me could not find an answer, they did not even cover that in my code change class.Thanks

Table 310.15(B)(2)(a) is used for branch circuits rated 15 or 20 amperes, and supplying only lighting or appliances that do not present overcurrent protection problems because of motor starting currents or other high starting currents.

Table 310.15(B)(2)(b) is used for all other branch circuits, such as those supplying motors or other loads that may have high starting currents.

Key Differences



Current Rating

Table 310.15(B)(2)(a) is limited to 15 or 20 amperes, while Table 310.15(B)(2)(b) is used for any current rating.


Purpose

Table 310.15(B)(2)(a) is specifically for lighting and appliances without high starting currents, while Table 310.15(B)(2)(b) is used for any type of load.

Example



Living Room

A 15-ampere branch circuit supplying only lighting and a TV (appliance with no high starting current) would use Table 310.15(B)(2)(a).


Garage:
A 20-ampere branch circuit supplying a heavy-duty drill (load with high starting current) would use Table 310.15(B)(2)(b). Flag for review