User: duck_huntr85, Location: Tennessee
Asked on: Thursday, February 24, 2011 at 10:49 pm EST
Answered on: Tuesday, May 14, 2024 at 2:01 am EDT
Question: Hey all,This is my first post of many im sure. Its great having a forum full of fellow electricians and people of related fields. So heres the issueMY boss and I were sizing out the Branch-circuit Short-circuit and Ground-fault protective device (which i will from now on abbreviate BC SC & GFP). WE have several 1hp 240v fan motors. I ran into "430.53 Several Motors or Loads on One Branch-Circuit". 430.53B states, verbatim:If the bc sc &gfp device is selected not to exceed that allowed by 430.52 for the smallest rated motor, two or more motors or one or more motors and other loads, with each having individual overload protection, shall be permitted to be connected to a branch circuit where it can be determined that the bc sc & gfp device will not open under the most severe normal conditions of service that might be encountered.There is no need to get into the math as i understand that. My problem is it says you cant exceed the rating of the bc sc & gfp device of the smallest motor sized according to 430.52 Not table 430.52 just 430.52.WE are going to use an inverse time breaker. Which is 250% of your FLC according to Table 430.52. That number allows us to have two motors on one 20 amp breaker, assuming it can handle the inrush of two motors starting at once. BUt there is an exception to table 430.52 which states the rating of an inverse time breaker can increase to but not exceed 400% of the FLC. Using that excepiton we could fit one more motor on a single circuit (assuming ofcoarse that the breaker could handle the inrush of all the motors starting). Could we use that exception based on how 430.53B is worded? And i mean in general not just for my specific instance.Thanks in advance for your replies
Yes, you can use the exception in Table 430.52 to increase the rating of an inverse time breaker to but not exceed 400% of the FLC when sizing the BC SC & GFP device under the conditions of 430.53B.
430.53B states that the BC SC & GFP device cannot exceed the rating allowed by 430.52 for the smallest rated motor. Table 430.52 provides the maximum rating of the BC SC & GFP device for various types of motors. However, there is an exception to Table 430.52 that allows the rating of an inverse time breaker to increase to but not exceed 400% of the FLC.By applying this exception, you can increase the rating of the BC SC & GFP device to accommodate more motors on a single circuit, provided that the breaker can handle the inrush current of all the motors starting at once. It is important to note that this exception is only applicable to inverse time breakers and not to other types of BC SC & GFP devices. Flag for review