User: uwireme, Location: Cottonwood, CA
Asked on: Friday, February 25, 2011 at 12:11 am EST
Answered on: Tuesday, May 14, 2024 at 2:02 am EDT
Question: This is a 3 phase sub-panel feed with 3-wire MN cable through a steel conduitWe dont need no stinking neutral...or do weWhy is it so hot
It is hot because you have a very high resistance connection at the neutral block. The highest resistance connection in the subpanel will cause the most heating. In this case, you have 3-wire MN cable feeding the subpanel. The neutral is connected to the neutral bar with a typical mechanical connection (pressure-plate type). All of the current flowing in the neutral conductor must pass through this connection. If the connection is not tight, or if the contact surfaces are dirty or corroded, the resistance of the connection will be high, which will cause the connection to heat up.In general, any time you have 3-wire MN cable feeding a subpanel, you should install a neutral bonding jumper between the neutral bar and the equipment grounding bar. This will provide a low-resistance path for the neutral current to flow, which will prevent the neutral connection from overheating. Flag for review