Question: I have a thread about this in the NEC so if a moderator needs to delet the one I understand. Anyhow, I have done my code change course from 2008 to 2011 and this was not discussed, actually till I was preparing a lesson for my class I did not even realize there was two tables in the 2011 code book. I for the life of me can not find an explaination for when to use one table over the other for derating conductor for amb. temp. (other than the obvious 86deg or 104degree) any insight I can get for myself and students would be greatly appreciated.Thanks
Table 310.15(B)(2) vs. Table 310.15(B)(3)
The two tables in the NEC for derating conductors for ambient temperatures are: Table 310.15(B)(2)
Derating Factors for 60°C to 90°C (140°F to 194°F) Conductors
Table 310.15(B)(3)
Derating Factors for 75°C to 110°C (167°F to 230°F) ConductorsThe key difference between the two tables is the type of insulation used on the conductors. Table 310.15(B)(2) applies to conductors with 60°C to 90°C (140°F to 194°F) insulation, while Table 310.15(B)(3) applies to conductors with 75°C to 110°C (167°F to 230°F) insulation.
When to Use Which Table
In general, you should use Table 310.15(B)(2) for: Conductors with insulation rated for 60°C to 90°C (140°F to 194°F) Conductors installed in enclosures, raceways, or other locations where the ambient temperature is likely to be between 60°C and 90°C (140°F and 194°F)You should use Table 310.15(B)(3) for: Conductors with insulation rated for 75°C to 110°C (167°F to 230°F) Conductors installed in locations where the ambient temperature is likely to be between 75°C and 110°C (167°F and 230°F)* Conductors installed in certain hazardous (classified) locations
Example:
If you have a cable with XHHW insulation (rated for 90°C), the derating factor for an ambient temperature of 86°F would be 0.86 from Table 310.15(B)(2), because 90°C is in the temperature range covered by that table.If you have a cable with THHN insulation (rated for 90°C), the derating factor for an ambient temperature of 104°F would be 0.70 from Table 310.15(B)(3), because 104°F is in the temperature range covered by that table. Flag for review