Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Grounding of two wire circuits

User: Castrovinci, Location: NJ

Asked on: Friday, February 25, 2011 at 7:57 am EST
Answered on: Tuesday, May 14, 2024 at 2:02 am EDT

Question: I have been searching the NEC for this and can't seem to find it. I will be replacing a ceiling fan for a customer that has only "two wire BX" circuits no ground. My question is do I take the ceiling fan ground and tie it in with the neutral or do I just leave it off. I was thinking a GFCI breaker but I have heard too much trouble with tripping issues. I don't do too much residential.Does anyone have an article number as well?

Article 404.9 - Grounding of EquipmentException No. 2

Equipment that is provided with a grounding terminal but is installed in a location where no grounding means exists is permitted to be connected, for equipment grounding purposes, to the metal electrical enclosure or raceway system of the equipment grounding conductor of the branch circuit supplying the equipment.

Interpretation

In this case, the ceiling fan is provided with a grounding terminal but there is no grounding conductor in the "two wire BX" circuit. Therefore, you are permitted to connect the fan's grounding terminal to the metal electrical enclosure or raceway system that is supplied by the equipment grounding conductor of the branch circuit.

Recommendation

Connect the ceiling fan's grounding terminal to the metal junction box that is supplied by the branch circuit's equipment grounding conductor. This will provide a path for fault current to flow to the electrical panel and prevent the fan from becoming energized if a fault occurs.

Note:
A GFCI breaker is not recommended in this situation because it may trip unnecessarily due to the inherent leakage current of the ceiling fan. Flag for review

Previous Question Next Question