Topic: Bakery load calculation

User: customelectric87, Location: Ohio

Asked on: Friday, February 25, 2011 at 8:51 am EST
Answered on: Tuesday, May 14, 2024 at 2:03 am EDT

Question: Guys-My customer wants an estimate on upgrading the wiring in a ex-barber shop. They plan to use the building as a small bakery. The existing service is 200A, 3 phase 120/208V with on 42 circuit panel. After reviewing article 220.20, I'm still a little unsure on the requirements. It's all electric, no gas. Can someone give me a load calculation example? I'm new to commerical work like this. Thanks.

Load Calculation Example for BakeryStep 1: Determine the Equipment Loads Oven: 30 kW Mixer: 10 kW Proofer: 5 kW Refrigerator: 2 kW Lighting: 3 kW Other appliances: 2 kWStep 2: Calculate the Total Load

Total Load = Sum of Equipment Loads = 30 kW + 10 kW + 5 kW + 2 kW + 3 kW + 2 kW = 52 kWStep 3: Apply Diversity Factor

Diversity factor (DF) accounts for the fact that not all equipment will be operating at full load simultaneously. For commercial buildings, a DF of 0.75 is typically used.Adjusted Load = Total Load x DF = 52 kW x 0.75 = 39 kWStep 4: Convert kW to kVA

kVA = kW / Power FactorAssuming a power factor of 0.85:kVA = 39 kW / 0.85 = 46 kVAStep 5: Calculate the Branch Circuit Loads

Based on the load calculation and Article 220.20, the following branch circuits are required: Two 3-phase, 4-wire, 208V circuits for the oven (30 kW or 40 kVA) Two 3-phase, 4-wire, 208V circuits for the mixer and proofer (15 kW or 20 kVA) One 3-phase, 4-wire, 208V circuit for the refrigerator and lighting (5 kW or 6 kVA) One 3-phase, 4-wire, 208V circuit for the other appliances (2 kW or 3 kVA)Step 6: Determine the Service Upgrade

The existing service is 200A, 3 phase 120/208V, which provides a total capacity of 48 kVA (200A x 208V x 1.732).The calculated load is 46 kVA. However, it is advisable to provide some buffer for future expansion.Therefore, a service upgrade to 60 kVA would be recommended.

Note: This is just an example, and the actual load calculation and service upgrade requirements may vary depending on the specific equipment and usage patterns. Flag for review