Topic: Compression Connector Lugs for Compact Conductors
User: Red Wiggler, Location: Camarillo, CA
Asked on: Friday, February 25, 2011 at 1:28 pm EST
Answered on: Tuesday, May 14, 2024 at 2:03 am EDT
Question: I am sure this question has been asked before...Can you use standard compression lugs on compressed copper conductors without downsizing the lug?Is there a crossover chart that covers both standard and compress conductors as far as the type of compression lugs?
## Using Standard Compression Lugs on Compressed Copper ConductorsNo, you cannot use standard compression lugs on compressed copper conductors without downsizing the lug.
Compressed conductors are designed to be smaller in diameter than standard conductors of the same ampacity. Standard compression lugs are designed to fit the standard conductor diameters. Using a standard compression lug on a compressed conductor will result in a loose fit, which can lead to high resistance and overheating.## Downsizing LugsTo use a standard compression lug on a compressed conductor, you must downsize the lug. Downsizing a lug means using a lug that is one size smaller than the conductor's nominal size. For example, if you have a compressed conductor that is equivalent to a 1/0 AWG conductor, you would use a 2/0 AWG compression lug.## Crossover ChartThe following table provides a crossover chart for standard and compressed copper conductors:| Compressed Conductor Size | Standard Conductor Size | Lug Size
8 AWG | 10 AWG | 10 AWG
4 AWG | 6 AWG | 6 AWG
1/0 AWG | 2/0 AWG | 2/0 AWG
| 2/0 AWG | 3/0 AWG | 3/0 AWG |
3/0 AWG | 4/0 AWG | 4/0 AWG
| 4/0 AWG | 250 kcmil | 2/0 AWG |
250 kcmil | 300 kcmil | 4/0 AWG
| 300 kcmil | 350 kcmil | 250 kcmil |
350 kcmil | 400 kcmil | 300 kcmil
| 400 kcmil | 500 kcmil | 350 kcmil |
500 kcmil | 600 kcmil | 400 kcmil
| 600 kcmil | 750 kcmil | 500 kcmil |
750 kcmil | 1000 kcmil | 600 kcmil || 1000 kcmil | 1250 kcmil | 750 kcmil |
Note: This chart is for general guidance only. Always consult the manufacturer's recommendations for the specific lug and conductor combination you are using.