User: mark32, Location: Currently in NJ
Asked on: Friday, February 25, 2011 at 1:30 pm EST
Answered on: Tuesday, May 14, 2024 at 2:04 am EDT
Question: After viewing the following pdf (Pages 123-127)http://www.pseg.com/business/builders/new_service/before/pdf/RequirementsElecSvc2005.pdfI have a question about the bonding of the troughs pictured. Lets first look at the diagram on pg 125. It shows a grounding block in the trough, I imagine one would need to use a bonding bushing on the conduit feeding the trough as well as the conduits feeding the meters, yes? Now look at the other 4 diagrams, to me, they all need to have such a grounding block in the trough but then again I have little experience in this area. Could anyone clear this up for me? Also, in these troughs, is there a tapped hole for a ground block, if not, is the metal substantial enough to tap let's say a 1/4-20 or larger bolt?
1. Bonding of TroughsDiagram on Page 125
Yes, bonding bushings are required on both the conduit feeding the trough and the conduits feeding the meters. The grounding block in the trough will connect the trough to the grounding system through the bonding bushings.
Other Diagrams
All of the other diagrams show troughs without a grounding block. However, the text on page 123 states that "The Service Trough shall be bonded to the grounding system with a ground strap or other acceptable method." This would indicate that a grounding block is required in all the troughs, even if it is not explicitly shown in the diagrams.
2. Ground Block Installation Troughs typically have tapped holes for ground blocks. If the trough does not have a tapped hole, it is acceptable to drill and tap a hole, as long as the metal is substantial enough. A 1/4-20 or larger bolt is acceptable for grounding purposes. Flag for review