User: andyandy, Location: 3 Hr 2 Min from Winged Horses
Asked on: Friday, February 25, 2011 at 5:21 pm EST
Answered on: Tuesday, May 14, 2024 at 2:04 am EDT
Question: My guys recently installed a back up generator and ATS on an 800 amp 3 phase 120/208 volt switch board. The client only wanted certain loads from the switchboard to energize during an outage. So what they did is took all of the breakers for the loads to be served from the generator and moved them to the bottom of the bussing in the switchboard. They cut the bussing above said breakers and tapped it with conductors rated at 800 amps and ranto the ATS which is rated at 800 amps and then ran conductors rated at 800 amps from the ATS back to the other half of the cut bussing. The project was inspected and approved by the AHJ. recently another EC saw the installation and raised a huge red flag tto the client and AHJ saying the install is not correct. Does anyone have any opinions on this? Code sections?
Concerns Raised
Potential for Overheating
The reduced bussing capacity at the bottom of the panel could lead to overheating under load, especially if there are multiple breakers operating simultaneously.
Short Circuit Protection
The lack of a dedicated busway or cables rated for the full 800 amp capacity could compromise short circuit protection for the circuit breakers below the cut-off point.
Code Requirements
NEC 408.16
Branch circuits supplied by an alternate source shall be isolated from other branch circuits of the same phase.
NEC 110.9
Conductors and raceways shall be rated to carry the maximum current of the load supplied.
NEC 408.22
Automatic transfer equipment shall be rated to carry the maximum current that will be drawn from it.
Assessment
While the installation was approved by the AHJ, it raises concerns about safety and code compliance. The following steps could be taken to address the issues:
Install a dedicated busway or cables
Run separate conductors rated for the full 800 amp capacity from the ATS to the circuit breakers being served.
Isolated the circuit breakers
Ensure that the circuit breakers below the cut-off point are isolated from other circuits of the same phase, either by using a dedicated busway or by installing a barrier between the two sections of bussing.
Verify short circuit protection
Calculate the available fault current at the bottom of the bussing and ensure that the circuit breakers and conductors are rated appropriately.
Conclusion:
The installation, as described, has potential safety hazards and may not fully comply with code requirements. It is recommended to address the concerns raised by the other EC by implementing the necessary modifications to ensure a safe and code-compliant system. Flag for review