Topic: Generator size vs. Service size question???

User: jango, Location: Massachusetts

Asked on: Saturday, February 26, 2011 at 11:20 am EST
Answered on: Tuesday, May 14, 2024 at 2:06 am EDT

Question: Can someone refer me to the NEC and also shed some info on the requirements of sizing a whole-house back up generator in relation to the actual service size? i.e. If I have a residence with a 400A service but the average annual draw is less than 150A on each phase, can the generator be sized smaller than 400A and still be code compliant? I do plan on using a 400A rated ATS but I'm hoping to be able to use a much smaller generator. I would appreciate as much input as possible. Thanks.

NEC Reference

[NEC 225.1](https://www.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=70) - Size of Overcurrent Devices

Sizing Requirements

As per NEC 225.1, the ampacity of the overcurrent device (in this case, the generator) must be not less than the noncontinuous load supplied by the generator.In your case, even though the average annual draw is less than 150A on each phase, the generator must be sized for the full 400A service. This is because the NEC does not permit a reduction in the size of overcurrent devices based on average load.

Reasons for Sizing to Service Size



Safety

The generator must be able to handle the maximum load that could potentially be drawn by the residence. A smaller generator could potentially overload and fail, creating a safety hazard.

Reliability

A generator that is sized too small may not be able to provide reliable power during an outage, especially if the load increases.


Future Expansion

A generator that is sized to the full service capacity will accommodate any future expansion of the electrical system without requiring a generator upgrade.

Use of ATS

You plan on using a 400A rated ATS, which is appropriate for a 400A service. The ATS will automatically transfer the electrical load from the utility grid to the generator during an outage.

Possible Exceptions

There may be some exceptions to the requirement of sizing a generator to the service size. However, these exceptions are typically limited to specific applications and require approval from the local authority having jurisdiction (AHJ).For example, in some cases, it may be possible to use a generator smaller than the service size if the following conditions are met: The generator is only used to power essential loads (e.g., lighting, refrigeration, medical equipment). The essential loads are carefully calculated and documented to ensure that they do not exceed the capacity of the generator.* The generator is equipped with overload protection to prevent damage in the event of a surge load.

Conclusion:


Generally, it is not code compliant to use a generator smaller than the service size for a whole-house backup application. However, you should consult with your local AHJ to determine if any exceptions apply to your specific situation. Flag for review