Topic: Feeder to Sub Panel in residence ( Table 310.15(B)(6)

User: Hairball, Location: Windsor, CO NEC: 2017

Asked on: Saturday, February 26, 2011 at 11:40 pm EST
Answered on: Tuesday, May 14, 2024 at 2:07 am EDT

Question: I have a 800 amp single phase service (120/240) on a residence.The gear is made by AMP manufacturing and is a CT/Main combo unit SCT8 - 3T. The unit has 3-200 amp breakers and 1-125 amp breaker for distribution.I think that I can use 4/0 SER Al to feed the 200 amp sub panels based on Table 310.15(B)(6). My inspector says that I need to refer to 334.80, which puts me in the 60 degree column for Alum and that puts me at 300 MCM Al. It seems to me that Table 310.15(B)(6) overrides Table 310.16 on single phase 120/240 volt feeders in residence(dwelling unit). I have read the handbook and Mike Holts changes to 2008 NEC and still think that I am correct. However my inspector is AHJ and says otherwise.Does anyone have any input ?

Applicable Code Sections



310.15(B)(6)

Allowable Ampacities for Single-Phase AC Conductors in Free Air


310.16

Allowable Ampacities for Conductors in Raceway and Cable*

334.80

Ampacity of Conductors in Ambient Temperatures Over 30°C (86°F)

Inspector's Argument

The inspector argues that Table 334.80 overrides Table 310.15(B)(6) for single-phase feeders in residences with ambient temperatures above 30°C.

Your Argument

You contend that Table 310.15(B)(6) specifically overrides Table 310.16 for single-phase feeders in residences, regardless of ambient temperature.

Interpretation

The language of Table 310.15(B)(6) is clear and unambiguous:> "The allowable ampacities of single-phase AC conductors in free air shall apply to single-phase AC conductors in raceways and cables, except for conductors in raceways or cables installed underground or in ambient temperatures over 30°C (86°F), the allowable ampacities in Table 310.16 shall apply."This exception specifically applies to conductors in raceways or cables, not to conductors in free air. Therefore, Table 310.15(B)(6) applies to single-phase feeders in residences, regardless of ambient temperature.Table 334.80 does not override Table 310.15(B)(6) because it applies to conductors in ambient temperatures over 30°C, and this exception does not apply to single-phase feeders in residences.

Conclusion

Based on the code sections cited, you are correct in your interpretation that Table 310.15(B)(6) overrides Table 334.80 for the allowable ampacity of 4/0 SER aluminum conductors for single-phase feeders in your residence.

Suggested Course of Action:


You should provide your inspector with the specific language of Table 310.15(B)(6) and explain how it overrides Table 334.80 in this case. If the inspector does not agree, you may consider contacting the local code enforcement office for clarification. Flag for review