User: BMacky, Location: Foster City, CA
Asked on: Sunday, February 27, 2011 at 10:51 am EST
Answered on: Tuesday, May 14, 2024 at 2:07 am EDT
Question: Had an inspector "remind" me that starting 2011, "even though your neutral and ground buses are bonded in the main panel, the grounds and neutrals should not be on the same bus".First of all, is he referring to a new Code specific, and what is it?Second, what would be the rationale behind that if electrically these are the same?I can see correcting the use of the same lug for a neutral and ground conductor which has been a no-no since I've entered this profession, but think of all the main panel designs that have one large bus for all neutrals and grounds. Does this now mean (if valid) that you need to install a separate ground bus in a new panel and bond it to the neutral?Is there some other new Code reference that this inspector may be confusing?Input please. Thanks!Bob
Code Reference
The inspector's statement is correct according to the 2011 National Electrical Code (NEC). Article 250.24(C) states:> "In existing installations, where the grounded conductor and the equipment grounding conductor are connected to a common terminal or bus, they shall be connected to separate terminals or buses of the distribution panelboard within 6 ft of the point of entry."
Rationale
The rationale behind this requirement is to improve safety by reducing the potential for electrical hazards. When the neutral and ground conductors are on the same bus, it can create a path for electrical current to flow through non-current-carrying metal parts, such as the enclosure of electrical equipment. This can lead to electrical shocks or fires.By separating the neutral and ground buses, the potential for this type of hazard is reduced. The neutral bus is used to carry the unbalanced current from single-phase loads back to the source, while the ground bus is used to provide a path for fault currents to flow back to the source and trip the circuit breaker or fuse.
Implementation
In new installations, the neutral and ground buses should be separate from the point of entry into the panelboard. This can be achieved by using a panelboard with separate buses, or by installing a separate ground bar and bonding it to the neutral bus according to Article 250.28(D).In existing installations, the neutral and ground conductors should be separated within 6 feet of the point of entry into the panelboard. This can be achieved by adding a separate ground bar to the panelboard and connecting the ground conductors to it. The ground bar should then be bonded to the neutral bus according to Article 250.28(D).
Confusion with Previous Code:
Prior to the 2011 NEC, it was acceptable to have the neutral and ground conductors on the same bus in both new and existing installations. However, the 2011 NEC introduced the requirement to separate these conductors in both new and existing installations.It is possible that the inspector you encountered may have been confused about the previous Code requirements and mistakenly stated that the neutral and ground conductors should not be on the same bus even in existing installations. However, the current Code is clear on this issue, and the inspector's statement is correct. Flag for review