Topic: Reclosing

User: jamesk, Location: NE (9.06 miles @5.9 Degrees from Winged Horses)

Asked on: Sunday, February 27, 2011 at 10:52 am EST
Answered on: Tuesday, May 14, 2024 at 2:07 am EDT

Question: I am a safety rep for a large utility and have a question around reclosing. Does anybody take the recloing feature off of underground cables for emp. who are performing work in eletric manholes/valuts on the cables that run through that manhole/vault? If so, which cables? All cables or just some? This has been a question around here for some time and just wondering if this has been explored.Thanks, Jamesk

Yes, it is common practice to take the reclosing feature off of underground cables for employees performing work in electric manholes/vaults.Which Cables?

The reclosing feature is typically removed for the following cables: Primary distribution cables (typically 15 kV or higher) Secondary distribution cables (typically 600 V or less) Service entrance cablesReasons



Preventing backfeed

Reclosing can energize a de-energized cable if it is backfed from another source, creating a hazard for workers.

Preventing overvoltages

Reclosing can cause dangerous overvoltages if the cable has a fault or is overloaded.


Protecting equipment

Reclosing can damage electrical equipment if it is not properly protected.

Procedure

The procedure for removing the reclosing feature varies depending on the specific utility and equipment. However, it typically involves:1. Isolating the cable to be worked on.
2. Removing the relay or fuse that controls reclosing.3. Installing a lockout/tagout device to prevent reclosing.


Additional Precautions

In addition to removing the reclosing feature, the following additional precautions should be taken:

Ground and test the cable
before starting work. Wear appropriate personal protective equipment (PPE), including rubber gloves, insulated tools, and arc flash clothing. Establish a safe work zone and clearly mark it with signs and barricades. Maintain clear communication with the control center.* Follow all applicable safety procedures and standards.

Note:

It is important to coordinate with the control center and other affected parties before removing the reclosing feature. This ensures that the system can be operated safely without compromising reliability. Flag for review