User: tomwible, Location: 3 Hr 2 Min from Winged Horses
Asked on: Sunday, February 27, 2011 at 11:47 am EST
Answered on: Tuesday, May 14, 2024 at 2:08 am EDT
Question: I am currently studying to take the NH Masters test. I am studying the codebook and using the Snapz course.Seems like there is some discrepancy with article 215 and the course. The Snapz has several questions in which the given answer says that continuous loads are calculated at 125% for load calcs. The article seems to say that continuous loads have their feeders sized at 125%.Which is it??? Loads calculated at 125% or 100%. Seems to me the code says circuits are sized at 125% but not for load calcs.Please help!!!!! Thanks in advance.-Tom
NH Masters Test: Article 215 Discrepancy
Article 215 of the National Electrical Code (NEC) addresses feeder calculations for continuous loads. There is a discrepancy between the NEC and the Snapz course regarding the percentage used for calculating continuous loads.
NEC Article 215:"Feeders supplying continuous loads shall have an ampacity of not less than 125 percent of the maximum load current computed in accordance with this article."Snapz Course:The Snapz course indicates that continuous loads are calculated at 125% for load calculations. This is not consistent with the NEC.
Correct Interpretation:According to the NEC, the continuous load is calculated at 100%, and the feeder supplying the load is sized at 125% of the calculated load current. This means that: Load calculations: Continuous loads are calculated at their actual wattage or amperage, without any multiplier. Feeder sizing: The feeder supplying the continuous load is sized at 125% of the calculated load current.
Example:A continuous load has a calculated current of 10 amps. The feeder supplying this load must have an ampacity of: Load calculation: 10 amps x 100% = 10 amps Feeder sizing: 10 amps x 125% = 12.5 ampsTherefore, a feeder with an ampacity of at least 12.5 amps would be required to supply this continuous load.
Recommendation:For the NH Masters Test, it is important to follow the requirements of the NEC. Remember that continuous loads are calculated at 100% for load calculations, and the feeder supplying the load is sized at 125% of the calculated load current. Flag for review