User: jarrydred, Location: Massachusetts
Asked on: Sunday, February 27, 2011 at 12:34 pm EST
Answered on: Tuesday, May 14, 2024 at 2:08 am EDT
Question: HiI have a question, is it possible to use a single phase 220VAC supply and use an inverter or VFD to convert to a 380VAC 3phase power, to run a milling machine and a lathe separatly ?- How much current will the single phase be drawing, the lathe has a 380VAC 5HP motor and the milling machine is a 380VAC 3HP motor, also if there is an inverter can you wire it up directly to the machine as if it was natural 3 phase 380VAC inputplease post links to inverter or VFD's if possibleThanks
Possible to Convert?
Yes, it is possible to convert a single-phase 220VAC supply to a 380VAC 3-phase power using an inverter or VFD (Variable Frequency Drive).
Current Draw
The current draw on the single-phase supply will depend on the efficiency of the inverter/VFD and the load. Assuming an efficiency of 85%, the current draw would be approximately: for 5HP motor: (5 HP × 746 W/HP) / (220 V × 0.85) = 19.9 A for 3HP motor: (3 HP × 746 W/HP) / (220 V × 0.85) = 12.0 AWiring
Yes, it is possible to wire an inverter or VFD directly to the machines as if it was a natural 3-phase 380VAC input. The inverter/VFD will generate the 3-phase waveform required to run the motors.
Inverter/VFD Options
Here are some links to inverters or VFDs that can convert a single-phase 220VAC supply to a 380VAC 3-phase power: Inverter
https://www.amazon.com/dp/B088Z69K1M
VFD
https://www.amazon.com/dp/B07MM9V94L
Note: Ensure that the inverter/VFD you choose is rated for the appropriate power and current requirements of your motors. Follow the manufacturer's instructions for wiring and configuration.* Consider using a dedicated circuit and appropriate wiring to handle the current draw. Flag for review