Question: I have a customer getting a hot tub that will be set outside on a stone patio. The manufacturer specifies that all wiring must be copper and that the EGC must be sized the same as the CCCs. Since they also require 50A OCP, it means that I can't use NM or UF anywhere in the run since the ground will be too small. It's about a 75' run from panel to disconnect to hot tub. The first 20 feet or so will be indoors above a dropped ceiling, the rest is outdoors under a deck and underground to the hot tub. Is pipe my only option or is MC an alternative? Locally I can get 6/3 MC with a #8 ground, and supposedly the sheath is a supplementary ground (page 9 here. Does that count to make the EGC the same size as the CCCs? Will the MC be in a damp or a wet location if it's strapped under the deck?Am I missing a better alternative?
MC Cable Usage
MC cable with a #8 ground and a metallic sheath that is used as a supplementary ground can be used for this installation. The metallic sheath meets the requirement for the EGC to be the same size as the CCCs.
Location of MC Cable
MC cable installed under a deck is considered a wet location. However, if the deck is well-ventilated and protected from moisture, it can be considered a damp location. Refer to the local electrical code for specific requirements.
Other Options
In addition to MC cable, you could also consider: Rigid metal conduit (RMC): Provides excellent protection for the conductors but is more expensive and difficult to install. Electrical metallic tubing (EMT): A less expensive option than RMC, but still provides good protection.
Recommendation
Based on the information provided, MC cable is a suitable option for this installation. It meets the code requirements for EGC sizing and is appropriate for wet or damp locations when properly installed.
Additional Notes Ensure that the MC cable is properly supported and protected from physical damage. Install rain-tight connectors where the MC cable enters the disconnect and hot tub. Use a watertight junction box if the MC cable is spliced outdoors. Inspect the MC cable periodically for damage, especially if it is exposed to moisture. Flag for review