Topic: 125amp feeder breaker in a 100amp main breaker panel

User: Ravenvalor, Location: Piedmont region of NC

Asked on: Monday, February 28, 2011 at 7:21 am EST
Answered on: Tuesday, May 14, 2024 at 2:09 am EDT

Question: Hello Friends,Is it permissible by the NEC to install a 125amp panel feeder breaker in a 125amp mainlug service panel that is back fed with a 100amp main breaker?Thanks,

No, it is not permissible by the NEC to install a 125 amp panel feeder breaker in a 125 amp main lug service panel that is back fed with a 100 amp main breaker.According to NEC 230.40 if a main breaker is installed on the line side of the main service disconnecting means, the main breaker shall be sized not to exceed the ampacity of the service conductors. In this case, the service conductors are rated for 100 amps, so the main breaker must be 100 amps or less. Flag for review