User: Michael.l.smith, Location: NE Nebraska
Asked on: Monday, February 28, 2011 at 8:31 am EST
Answered on: Tuesday, May 14, 2024 at 2:09 am EDT
Question: Does 110.26(A)(1) apply to a motor disconnect if I can lock out a controller which feeds the disconnect prior to opening the safety switch/disconnect? The controller is designed to be locked out and isolates all power sources to the disconnect.
Yes, 110.26(A(1) says "automatic disconnect shall be provided for equipment located in a remote location or out of sight of the operator."The controller described in the question is not a disconnect and does not meet the requirements of 110.26(A)(1). Flag for review