Topic: Load Calculation for Single Family Dwelling Unit

User: duck_huntr85, Location: Chapel Hill, NC

Asked on: Monday, February 28, 2011 at 10:07 am EST
Answered on: Tuesday, May 14, 2024 at 2:09 am EDT

Question: Hey all,Im doing some example calculations for single family dwellings. But in the example it says the dwelling unit has baseboard heaters that draw 18kVA and a heat pump that draws 6kVA. When doing the calc. for the heating/AC system I know you are supposed to omit the smaller of the two but i dont know if that applies here. What am i supposed to do with the heat pump? Thanks in advance for your response.

In this case, you should omit the smaller load, which is the heat pump in this instance. The reason for omitting the smaller load is to account for redundancy in the heating system.Since the dwelling unit has both baseboard heaters and a heat pump, it's likely that the heat pump is used as a supplementary heating source. In the event that the heat pump fails, the baseboard heaters would still be able to provide heating for the dwelling unit.Therefore, to calculate the heating/AC system load, you would use the baseboard heaters' load of 18kVA. Flag for review