Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: SO cord connected to switches

User: Dgator, Location: 3 Hr 2 Min from Winged Horses

Asked on: Monday, February 28, 2011 at 10:37 am EST
Answered on: Tuesday, May 14, 2024 at 2:10 am EDT

Question: I recentley had an installation for exterior low votage lighting. Using step down transformers that came with a cord and cap to plug into an outlet. I removed the cord cap and wired it directly, using a strain relief connector in the box and to a switch as a means of disconnect. The inspector turned it down citing it was against the code to connect SO cord to a switch. He did not refer to a certain section of the code. Is there anything in the code (2008) against the type of installation?

Yes, there is something in the 2008 NEC against the type of installation you described.

NEC 400.2 states, "Flexible cords and cables shall be used only for pendants, wiring of fixtures, appliances, and other utilization equipment, where the flexible cord or cable is the connecting means between the fixed wiring of the structure and the equipment."Since the cord is being used to connect the transformer to the switch, which is not a utilization equipment, it violates this code rule.The inspector was correct in rejecting the installation. You will need to rewire the system using a permanent wiring method, such as Romex or conduit. Flag for review

Previous Question Next Question