Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: fixed heat calculation

User: M. D., Location: NJ/PA

Asked on: Monday, February 28, 2011 at 4:12 pm EST
Answered on: Tuesday, May 14, 2024 at 2:11 am EDT

Question: Lets' see , I've got 4250 watts of fixed heat divided by 240v = 17.7 amps x 1.25 for continuous load = 22.13 amps ,. Lets call it 23 amps . 12\2 nmb is good for 25 amps @ 60 deg. there will be no insulation my question is can I use a 20amp breaker on this circuit? it should never see more than 18. amps ? the wire is good for 25 .Also I live in Massachusetts where we have this:334.80 Ampacity. Type NM, NMC, and NMS cable shall have conductors rated at 90?C(194?F).Where installed in thermal insulation, the ampacity of conductors shall be that of 60?C(140?F) conductors. The ampacity of Types NM, NMC, and NMS cable installed in cable trayshall be determined in accordance with 392.11.

According to the 2020 NEC, a 20-amp breaker can be used on a circuit with 122 NMB wire, as long as the load does not exceed 80% of the breaker's rating. In this case, the load is 23 amps, which is greater than 80% of 20 amps (16 amps). Therefore, a 20-amp breaker cannot be used on this circuit.The ampacity of the conductors in this circuit must be derated to 60°C because the conductors are installed in thermal insulation. The ampacity of 122 NMB wire at 60°C is 25 amps.A 25-amp breaker would be the correct size for this circuit. Flag for review

Previous Question Next Question