User: dasarmin, Location: Texas
Asked on: Monday, February 28, 2011 at 5:59 pm EST
Answered on: Tuesday, May 14, 2024 at 2:11 am EDT
Question: How do you calculate the Neutral Current in a 4Wire 3Phase 277Vac circuit.For example, 15 parking lot pole lamps @ 400Watts each and pf of 0.88 will be powered from a 3phase 277Vac Lighting Panel.I believe the total current would 6000 / 277 * 0.88 = 25Amps. Each phase wouild be balanced to carrier less current than the total current, say 5 lamps per phase for approximately 8.2Amps per phase.But the Neutral should be sizes (wire size) to carry 25Amps.Is this thought process correct?FYI, each lamp is rated at 1.7Amps continuous.
Step 1: Calculate the Total Current
Total current = Total power / Voltage / Power factorTotal current = 6000 W / 277 V / 0.88Total current = 27.36 AStep 2: Calculate Phase Currents (Balanced Load)Phase current = Total current / Number of phasesPhase current = 27.36 A / 3Phase current = 9.12 AStep 3: Determine if the Neutral Carries CurrentIN = √(Ia² + Ib² + Ic²)where Ia, Ib, and Ic are the phase currents.IN = √(9.12² + 9.12² + 9.12²)IN = 16.03 AConclusion: