Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: transformer Calculations

User: xformer, Location: Dallas, Tx

Asked on: Monday, February 28, 2011 at 6:40 pm EST
Answered on: Tuesday, May 14, 2024 at 2:11 am EDT

Question: So for a transformer with Primary and Secondary OCPD, The primary OCPD is based upon the 125 % of the Primary Current with the option to go up to 250 % as permitted in the second half of of table 450.3(B) ? And if I increase OCPD must I then resize my primary conductors?

Primary OCPD

Yes, the primary OCPD can be based on 125% of the primary current, with the option to go up to 250%, as allowed in the second half of Table 450.3(B).

Sizing of Primary Conductors

If you increase the OCPD, you may need to resize the primary conductors. This is because the conductors must be able to carry the increased current without overheating.The following formula can be used to determine if the primary conductors need to be resized:

I = OCPD / (125% x Primary Current)
Where: I = Ratio of OCPD to 125% of primary current OCPD = Overcurrent protective device rating* Primary Current = Nameplate current of the transformerFor example, if you have a transformer with a primary current of 100 amps and you increase the OCPD to 200 amps, the ratio would be 200 / (125% x 100) = 1.6. This means that the primary conductors would need to be resized to handle 1.6 times the original current.

Recommendation

It is recommended to consult with a qualified electrician to determine the appropriate size of OCPD and conductors for your specific application. Flag for review

Previous Question Next Question