Question: The 2011 NEC code states that all portable generator, 15 kW or less, shall have GFCI protection for 15, 20 and 30 amp (120/240 vlot) receptacles. The code does not say any thing about welders or generator on trailers (ex. 7kW). Are they considered exempt or do they have to comply.If it needs to comply, what should the minimum milliamp trip rate 5mA or 30 mA?Your help is grealty appreciated.
Welder Generators
Welder generators are portable generators that are specifically designed for arc welding applications. They provide a high current output, typically in the range of 100-250 amps, at a low voltage (typically 25-35 volts).
NEC Code Applicability
The NEC does not specifically exempt welder generators from the GFCI protection requirement for portable generators. However, there are two potential arguments for exempting welder generators:1. Welder generators are intended for commercial use. The NEC GFCI requirement applies to "consumer products," which are defined as products intended for use by the general public. Welder generators are typically used by professional welders and are not intended for general household use.2. The high current output of welder generators makes GFCI protection ineffective. GFCIs are designed to trip when there is a difference in current between the hot and neutral conductors. However, the high current output of welder generators can override the tripping mechanism of GFCIs.
Industry Practice
Despite the lack of a specific exemption in the NEC, it is common industry practice to install welder generators without GFCI protection. This is because of the potential issues discussed above.
Conclusion
Based on the above discussion, it is likely that welder generators are not required to have GFCI protection under the NEC code. However, it is important to consult with a qualified electrician to determine the specific requirements for your application.
Trailers
The NEC does not differentiate between portable generators that are mounted on trailers and portable generators that are not. Therefore, portable generators on trailers must comply with the same GFCI protection requirements as portable generators that are not on trailers.
Minimum Milliamp Trip Rate
The NEC requires GFCIs to have a minimum trip rate of 5mA for personnel protection. Flag for review