Topic: 'Small' flexible aluminum connections

User: tshephard, Location: San Jose, CA

Asked on: Monday, February 28, 2011 at 8:14 pm EST
Answered on: Tuesday, May 14, 2024 at 2:11 am EDT

Question: Hi all -thanks for any input...Changing a 240V cooktop, calls for 40 amp circuit, manual instructs special procedures if supply is also aluminum (such as copper pigtail between ALs). I have #6 AL SE XHHW to jb for old stove - no problem with ampacity.The cooktop comes with 6 feet of #10 aluminum XLPE (seems OK for OEM), with about 50 strands (in FMC). As I read, I seem to crossed a flexible conductor limit. But my supply guys act like I'm the only one ever to ask for flex, dual rated connectors.Am I researching this right, or have I overlooked something obvious? Am I making this too complicated? Would split bolts (Al/Al type) inherently be flex rated? Is that flex rating only for screw and crimp types connectors or for all? What's really different physically in a flex connector?I wonder because the listed device does call for special connections because of Al/Al hazard, but never mentions the high flexibility of the conductor as a special consideration.Another thing that bothers me is that the FMC on the cooktop came with nice, neat rubberized cloth tape around the conductors (as though for neatness), and then explictily covering the end of the FMC where it would go into a flex connector for about 2 inches - as though to prevent any grounding to the connector at the box.I have cut through the tape for flex connector continuity, and used the old purple CU/AL wirenuts as I look for the right or best connectors.Any help?

#6 AWG Aluminum SE XHHW to JB for the old stove is rated for 55 amps, so it is OK for a 40-amp circuit.The cooktop comes with 6 feet of #10 AWG aluminum XLPE (cross-linked polyethylene) with about 50 strands (in FMC). This conductor is rated for 30 amps, which is less than the 40-amp circuit requirement.Flexible conductors are rated for use in flexible applications, such as where the conductor is subject to movement or vibration. The flexible conductor that comes with the cooktop is intended for connection to the cooktop terminal block, which is not a flexible application. Therefore, the use of a flexible conductor in this application is not a violation of the code.Split bolts (Al/Al type) are not inherently flex rated. Flex rated connectors are designed to maintain electrical continuity under flexing conditions. Split bolts are not designed for this purpose.The rubberized cloth tape around the conductors is intended to protect the conductors from abrasion and moisture. It is not intended to prevent grounding to the connector.I recommend that you use the following connectors: For the connection between the #6 AWG Aluminum SE XHHW and the #10 AWG aluminum XLPE, use a dual-rated crimp connector that is rated for both aluminum and copper conductors. For the connection between the #10 AWG aluminum XLPE and the cooktop terminal block, use a crimp connector that is rated for aluminum conductors.Make sure that all connections are tight and secure. Flag for review

Previous Question Next Question