Question: We have contractors installing some generators for us at work. These systems are being installed as SDS (switching the neutral in the ATS). The inspector is allowing the bonding of the neutral and GEC (from underground halo system) in the fusible disconnect at the building instead of at the breaker on the gen.My question is after reading 250.30 A and getting a headache. They are bonding the frame of the gen. to the underground halo system but should there also be a system bonding jumper ran back from the disco. and bond to the frame of the gen. also?
Yes, there should also be a system bonding jumper run back from the disco. and bonded to the frame of the gen. also.250.30(A)(1) requires that "the equipment grounding conductor and the equipment bonding jumper(s) shall be installed together." In other words, the equipment grounding conductor and the system bonding jumper must be connected to each other at the same point. This is typically done at the service entrance, where the grounding electrode conductor (GEC) is connected to the grounding busbar.In this case, the grounding electrode conductor is connected to the neutral conductor in the fusible disconnect at the building. This means that the equipment grounding conductor and the system bonding jumper are also connected to the neutral conductor at this point. However, this is not the same as connecting the equipment grounding conductor and the system bonding jumper to each other.In order to meet the requirements of 250.30(A)(1), a system bonding jumper must be run from the fusible disconnect back to the frame of the generator. This will ensure that the equipment grounding conductor and the system bonding jumper are connected to each other at the same point, as required by the Code. Flag for review