Topic: Apartment electrical service ground and bonding help needed

User: ohms277, Location: Ohio

Asked on: Monday, February 28, 2011 at 9:04 pm EST
Answered on: Tuesday, May 14, 2024 at 2:11 am EDT

Question: Power is coming underground up into a 600 amp. 2 pole fused disconnect. From the load side of this switch power goes into r/t gutter where it is pdb'd and feeds nine meter cans with 100 amp. disconnects beneath each meter. From each 100 amp. disconnect a #2/3 with #4 ground SER cable goes to a apartment. One of the meters is for the house. In each disconnect the ground and neutrals are seperated. A 1/0 grounding electrode conductor goes from the ground rod to the ground lug in the 600 amp. disconnect and then to the r/t gutter where it is attached to mechanical lug, and then (6) #6 have been taken to each meter sockets neutral terminal as per the electric utility's requirements. The grounding conductor is bonded to the neutral in the 600 amp. disconnect. Don't I now have a dual bonding situation? Is this safe and or legal?Any input would be greatly appreciated.

Dual Bonding Situation

Yes, you have a dual bonding situation in your electrical system. Dual bonding is when the grounding conductor (ground rod) is connected to both the neutral and the equipment grounding system in the main service panel.

Safety and Legality

Dual bonding was once considered acceptable but is now discouraged by the National Electrical Code (NEC) and prohibited in some jurisdictions. This is because dual bonding can create dangerous ground loops and overvoltage conditions in the event of a fault.

NEC Requirements

The NEC requires that the grounding conductor be connected to the equipment grounding system and to the neutral at the service entrance. However, it does not allow for the neutral to be bonded to the equipment grounding system anywhere else in the system.

Recommended Solution

To eliminate the dual bonding situation and ensure compliance with the NEC, you should:1. Disconnect the grounding conductor from the neutral in the 600 amp disconnect.2. Install a separate ground bar in the r/t gutter.3. Connect the grounding conductor from the ground rod to the ground bar.4. Connect the neutral conductors from the meter sockets to the neutral bar in the r/t gutter.5. Connect the equipment grounding conductors from the 100 amp disconnects to the ground bar in the r/t gutter.By following these steps, you will isolate the grounding and neutral systems and eliminate the dual bonding situation.

Additional Considerations Check with your local electrical inspector to ensure that the proposed solution complies with local codes and regulations. Do not attempt to perform any electrical work unless you are qualified and licensed to do so. Flag for review