User: PDK, Location: Chapel Hill, NC
Asked on: Tuesday, March 1, 2011 at 11:25 am EST
Answered on: Tuesday, May 14, 2024 at 2:13 am EDT
Question: Is there any code reference for when and when not a wall penetration should be sleeved regardless if it is fire rated or not.
National Electrical Code (NEC)Article 300.22(C) Sleeving Required
Conductors passing through holes in fire-rated walls, partitions, or floors shall be protected by approved sleeves having fire-resistant ratings not less than that required for the opening through which they pass.
Exceptions
Where the opening is formed by metal studs or joists. Where the opening is protected by factory-installed grommets or bushings with fire resistance ratings not less than that required for the opening. Where the conductors are in metal raceways or cable assemblies with fire resistance ratings not less than that required for the opening. Where the conductors are Type MC cables with a fire resistance rating not less than that required for the opening.
Article 300.22(D) Sleeving Not Required
Sleeves shall not be required where any of the following conditions apply: The conductors are paralleled and separated by a continuous and firmly fixed barrier, such as a stud or joist. The opening is completely filled with nonflammable materials, such as cement or gypsum. The opening is sealed with a fire-resistant material, such as a fire-rated caulk or foam. The conductors are Type MI cables or rigid metal conduit.* The conductors are installed in a special-purpose fire-rated enclosure, such as a fire-rated junction box or conduit body.
National Fire Protection Association (NFPA) 70: National Electrical CodeSection 300.22 Sleeving Required(Same as NEC Article 300.22(C))Exceptions
(Same as NEC Article 300.22(C) Exceptions)
Section 300.22 Sleeving Not Required(Same as NEC Article 300.22(D)) Flag for review