User: ron, Location: New York, 40.7514,-73.9925
Asked on: Tuesday, March 1, 2011 at 3:46 pm EST
Answered on: Tuesday, May 14, 2024 at 2:13 am EDT
Question: 240.4 clearly indicates that conductors need to be protected against overcurrent in accordance with their ampacities ....It specifically refers to 310.15 which is 0-2000V.Where is the requirement for overcurrent and/or short circuit protection for conductors >2000?240.4 doesn't specifically exclude conductors >2000V, but the reference to 310.15 leaves me with nothing to go by.I have a 15kV feeder that I will protect with 50/51 protection (overcurrent and short circuit protection), but I'm trying to figure out for this vveerryy long radial campus feeder whether there is any way I can reduce the ampacity of the feeder as I go along from building to building and the calculated load is less and less.Thanks
Overcurrent Protection for Conductors >2000V
The requirement for overcurrent protection for conductors over 2000V is found in Article 490 of the National Electrical Code (NEC).
NEC 490.21(B)(1) requires conductors over 2000V to be protected against overcurrent in accordance with their ampacities and the overcurrent device ratings specified in Tables 490.21(B)(1) and 490.21(B)(2).
NEC 490.21(B)(1) Table provides ampacity multipliers for specific conductor sizes and types over 2000V. These multipliers are used to reduce the allowable ampacity of the conductor at higher voltages.
Example
For a 500 kcmil copper conductor, the ampacity at 2000V is 900A. However, at 15kV, the ampacity is reduced to 900A x 0.84 = 756A (based on the multiplier from Table 490.21(B)(1)).
Reducing Conductor Ampacity Over a Radial Feeder
To reduce the ampacity of a conductor over a radial feeder, you can use the following methods: Install overcurrent protection devices at each building
This will protect the conductors from overcurrent between the buildings.
Use conductor sizes based on the calculated load at each section of the feeder
This will reduce the conductor ampacity as the load decreases.*
Install voltage regulators: This can help maintain a consistent voltage along the feeder, allowing for smaller conductor sizes.However, note that reducing the conductor ampacity may also require additional overcurrent protection devices or voltage regulators to ensure proper protection. It is important to consult with a qualified electrical engineer to determine the appropriate conductor ampacity and protection measures for your specific application. Flag for review