Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Article-517

User: anbm, Location: Fl

Asked on: Tuesday, March 1, 2011 at 7:19 pm EST
Answered on: Tuesday, May 14, 2024 at 2:14 am EDT

Question: We have a main emergency distribution panel 'A' fed out of an emergency generator.Distribution panel 'A' feeds existing panel 'B'. Panel 'B' feeds (4) ATSs (critical, life-safety and two equipment branch ATSs).Is it legal to feed above ATSs from a panel downstream of main emergency panel?

Yes, it is legal to feed the ATSs from a panel downstream of the main emergency panel, provided that the following conditions are met: Adequate capacity

The downstream panel must have sufficient capacity to handle the load of the ATSs and any other loads connected to it.


Proper overcurrent protection

The downstream panel must be equipped with overcurrent protection devices (e.g., circuit breakers or fuses) that are sized appropriately for the load of the ATSs.

Selective coordination

The overcurrent protection devices in the downstream panel must be selectively coordinated with the overcurrent protection devices in the main emergency panel. This means that the downstream devices will trip before the main emergency panel devices, ensuring that only the affected circuit is isolated in the event of a fault.


Compliance with NEC

The installation must comply with all applicable sections of the National Electrical Code (NEC), including Article 700 for emergency power systems.In addition to these requirements, it is important to consider the following factors:

Reliability

The downstream panel should be located in a protected area where it is less likely to be damaged or compromised during an emergency.


Accessibility

The downstream panel should be easily accessible for maintenance and testing.*

Labeling:
The downstream panel should be clearly labeled to indicate that it is part of the emergency power system.By following these guidelines, you can ensure that the ATSs are properly protected and that the emergency power system is reliable and safe. Flag for review

Previous Question Next Question