Topic: sizing EBJ Vs ECG

User: vanvan, Location: Chapel Hill, NC

Asked on: Wednesday, March 2, 2011 at 1:00 am EST
Answered on: Tuesday, May 14, 2024 at 2:14 am EDT

Question: Hello... quick ? on a debate we had at work. We have a 30amp circuit which we had to upsize the conductors to #8. Per 250.122 (B) we have to upsize the EGC as well, so we did accordingly. Well we came to a point where we had to make a splice and while bonding to our splice box some of us thought we could just use a #10 pig tail tied to our #8's. While others thought it had to be jumpered with a #8. 250.102 (D) doesnt state anything about upsizing a EBJ, just that it has to be sized in accordance with table 250.122. I'm not finding anything that says we have to upsize a #10 pigtail to #8 for this splice box. Any ideas on who is correct? Think we maybe reading too much into this but sure is a lot easier to screw in a 10 pigtail.Thanks so much for any input!

According to the 2020 National Electrical Code (NEC), you are correct in your interpretation. Section 250.102(D) does not require an equipment bonding jumper (EBJ) to be upsized when spliced to a larger conductor. As long as the EBJ is sized in accordance with Table 250.122, it is acceptable to use a #10 pigtail even if the main conductors are #8.Therefore, those who believe that the EBJ must be #8 are mistaken. The NEC does not require this, and it would be unnecessary to upsize the EBJ in this case. Flag for review