Topic: Help specifying parts for terminating 3-phase cables to a safety switch

User: mienime2488, Location: Los Angeles, Ca

Asked on: Wednesday, March 2, 2011 at 12:56 pm EST
Answered on: Tuesday, May 14, 2024 at 2:16 am EDT

Question: Hi everyone. I am a junior engineer specifying parts for a 3-phase safety switch termination. I have some exposure to industrial wiring but not enough experience to be fully confident of the parts I choose. I am the only EE in an office of MEs, and it's hard to find someone to guide me. Any help would be greatly appreciated!I am working with a cable that has six 1/0-conductors that will be used to carry 3-phase 440 V in a marine environment. These conductors are going to be terminated to a heavy-duty safety switch.Here are my questions.I'm working with Square D Safety Switches. If I want fusible switches, I am limited to three fusible, switched poles with groundable neutral. If I am supposed to use the six conductors to carry the 3-phase, how would I terminate six conductors to this? Would I need two panels? Or should I consider the six not fusible, no neutral panel?If this is too elementary, and I should be reading things up on my own, could someone suggest some reading material?Thanks in advance!

Terminating Six Conductors to a Fusible Switch

Since the available fusible switches have only three poles, you will need two switches to terminate all six conductors. Each switch will terminate three conductors, allowing you to control each phase separately.

Two Switches Required

You will need two Square D fusible switches with three poles each, such as the DFPK123L400 series. These switches have groundable neutral poles that can be used for the fourth conductor.

Wiring Configuration Wire the three phases (L1, L2, L3) to three poles of one switch. Wire the groundable neutral (N) to the neutral pole of the same switch. Wire the remaining three conductors (phases A, B, C) to three poles of the second switch. Ground the remaining neutral pole of the second switch.

Non-Fusible Option

If you prefer a non-fusible switch, you can use Square D DPFK122L400 series switches. These switches do not have fusible poles, so you will need to install separate fuses upstream of each switch.

Reading Material Square D Safety Switch Catalog: https://www.se.com/ww/en/product-category/3428-safety-switches/ NEC (National Electrical Code) Article 409: https://www.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=70* "Industrial Wiring Guide" by Rex Wilson: https://www.amazon.com/Industrial-Wiring-Guide-Rex-Wilson/dp/1607504940 Flag for review