Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Splicing EGC

User: liverpool, Location: Portland, Oregon

Asked on: Wednesday, March 2, 2011 at 1:51 pm EST
Answered on: Tuesday, May 14, 2024 at 2:16 am EDT

Question: Does the NEC take exception to splicing equipment grounding conductor running with phase conductors in a conduit? I have a client design criteria which prohibits splicing any ground conductors. I wanted to verify if NEC agrees before challenging the client requirement.

NECArticle 250.30(A)(1) states that:> "An equipment grounding conductor shall extend to each outlet, switch, or junction box and will be connected to the box."Article 250.30(A)(3) states that:> "Equipment grounding conductors shall be permitted to be spliced at junction boxes or other accessible points."Conclusion

The NEC does not take exception to splicing equipment grounding conductors running with phase conductors in a conduit. In fact, it explicitly permits it in Article 250.30(A)(3).

Client Design Criteria

The client's design criteria that prohibits splicing any ground conductors is more restrictive than the NEC. You can challenge this requirement by citing the relevant NEC articles.

Recommendation

It is recommended that you discuss this issue with the client and provide them with a copy of the NEC articles. Explain that the NEC permits splicing equipment grounding conductors, and that prohibiting it may compromise the safety and reliability of the electrical system. Flag for review

Previous Question Next Question