Question: Ive had an ongoing discussion with a coworker, the boss and an inspector about Home Depot rating #6 aluminum SE cable for 60 amps. The inspector says 50 amps. My coworker wants to use an existing SE cable for a subpanel and we both think it needs to be on a 40 amp breaker. Im not sure who is wrong but I would appreciate any insight.
Electrical Code Requirements
According to the National Electrical Code (NEC), the ampacity of #6 aluminum SE cable is 55 amps at 75°C. However, this ampacity is subject to adjustment based on specific application factors, such as ambient temperature and number of conductors in the cable.
Application Factors
In this case, the application factors to consider are: Ambient temperature
If the cable is installed in a high-temperature environment, the ampacity must be derated.
Number of conductors
If the cable is installed with other conductors in the same conduit or raceway, the ampacity must be reduced.
Inspector's Determination
The inspector has likely considered these application factors and determined that the ampacity of the #6 aluminum SE cable in your case is 50 amps. This is a reasonable determination based on typical installation conditions.
Coworker's Position
Your coworker's position that the cable should be on a 40 amp breaker is also reasonable. While the cable is rated for 50 amps, it is always recommended to use a breaker that is slightly undersized to account for potential overloads or other factors that could reduce the cable's capacity.
Conclusion
Based on the NEC requirements and the application factors, the following conclusions can be drawn: Inspector's determination
The inspector is correct in stating that the #6 aluminum SE cable should be rated for 50 amps in this application.
Coworker's position: While the coworker's position is not incorrect, it is generally advisable to use a breaker that is slightly undersized to ensure safety and prevent damage to the cable.Therefore, it is reasonable to use the #6 aluminum SE cable on a 40 amp breaker, as it is undersized for the cable's rated ampacity. Flag for review