Topic: 450.22

User: charlie b, Location: Lockport, IL

Asked on: Wednesday, March 2, 2011 at 4:45 pm EST
Answered on: Tuesday, May 14, 2024 at 2:16 am EDT

Question: Consider a pad-mounted, outdoor, dry-type transformer in excess of 112.5 KVA. The site plan shows a fuel oil tank and a gas tank (I don?t know if ?gas? is gasoline or propane or something else) a few feet away. 450.22 tells me I only need to keep the transformer 12 inches away from combustible materials. But does that only refer to a combustible surface of the exterior wall of a nearby building? I don?t know if there is another relevant code section. I would not call this ?classified area,? under the 500-series articles, particularly since it is outdoors. Can we not postulate a short circuit failure within the transformer that could create an ignition source for a nearby fuel oil tank? Is there some other code that would mandate a minimum separation?

NEC 450.22

NEC 450.22 states that transformers rated over 112.5 kVA "shall be installed at least 12 inches from combustible materials." This requirement applies to all dry-type transformers, regardless of their location.

Other Relevant Code Sections

There are no other code sections that specifically address the minimum separation distance between dry-type transformers and combustible materials. However, the following code sections may be relevant: NEC 300.3(B) requires that electrical conductors and equipment be installed in a manner that "will not promote the spread of fire." NEC 450.45 requires that dry-type transformers be "installed in a vault or enclosure to prevent the escape of fire."Classified Areas

The area around a dry-type transformer is not considered a classified area under the NEC 500 series articles because it is not a location where flammable or combustible materials are handled, processed, or stored.

Ignition Source

A short circuit failure within a dry-type transformer could create an ignition source. However, the transformer is designed to contain any fire that may occur. The 12-inch separation distance required by NEC 450.22 provides a sufficient buffer zone to prevent the ignition of nearby combustible materials.

Conclusion

Based on the NEC, the minimum separation distance between a pad-mounted, outdoor, dry-type transformer over 112.5 kVA and a combustible material, such as a fuel oil tank, is 12 inches. This requirement ensures that the transformer will not be a potential ignition source for nearby combustible materials. Flag for review