User: drv72388, Location: Portland, Oregon
Asked on: Wednesday, March 2, 2011 at 6:55 pm EST
Answered on: Tuesday, May 14, 2024 at 2:17 am EDT
Question: If you have a parallel run of 3 sets of 500 kcmill wires in separate raceways what size grounding/bonding wire is required to be ran?Need clarification on Art. 250.30 (A)(8)(a) and (b)
Article 250.30(A)(8)(a) and (b) states: (a) When multiple conductors are installed in parallel and connected in parallel at both ends, bonding together the neutral conductors is acceptable in lieu of running a dedicated grounding conductor, provided that all the following conditions are met: The conductors are not more than 20 feet in length. The conductors are of the same size and type. The conductors are part of the same circuit. (b) When multiple grounding or bonding conductors are installed in parallel, they shall be connected in parallel at both ends.
In your case
You have 3 sets of 500 kcmil wires in separate raceways, which is not covered by the conditions in (a). Therefore, you
cannot use the neutral conductors for grounding/bonding.Instead, you must follow (b) and install a separate grounding/bonding conductor in parallel with each set of phase conductors. The size of the grounding/bonding conductor is determined based on the size of the phase conductors, as per Table 250.30(A)(1): For 500 kcmil phase conductors, the grounding/bonding conductor must be at least 250 kcmil.
Conclusion:
You must run a separate 250 kcmil grounding/bonding wire in parallel with each set of 3 x 500 kcmil phase conductors. Flag for review