Topic: Single Phase service labeled as three phase

User: acolella, Location: MidWest

Asked on: Wednesday, March 2, 2011 at 6:56 pm EST
Answered on: Tuesday, May 14, 2024 at 2:17 am EDT

Question: I am surveying a job site to install A/C equipment in a very old manufacturing facility. Approximately 1930s-1940s. When I was in the facility today I noticed something very strange.What I see outside is a single phase of 7620 Volts and a neutral conductor going underground from the pole in to a transformer vault in the buildings basement.I can absolutely confirm that there is only a single phase and a neutral going to the vault from the pole outside. However, the switchboard leaving the vault has "240 Volts Three Phase" labeled on it and on every disconnect downstream of that switchboard. The transformer vault is locked by the utility company so I can not get in there at this time. I had no tools or test equipment with me today but plan on returning with some within the next few days. Can somebody tell me if they have ever seen anything like this before? Or if it is even possible to derive three phase power from this type of connection.I would like to fully understand this type of system before we start installing, or even purchasing for that matter, three phase equipment. This building has three services, two of which I have worked with before. (Today was my first day in the older section of the building) One service is 480V 600A Ungrounded Delta (which I have confirmed) fed from a pad mounted unit substation. The other service is 240V 400A Ungrounded Delta (which I have also confirmed) fed from three cans on a pole outside of the building. But the third (and oldest) service is labeled as "240V Three phase" which clearly only has a single phase and neutral going into the vault. We would prefer to utilize this three phase service (if it is in fact three phase) that is in question, due to its proximity to the location of where the A/C units need to be installed, rather than run some 400-500 feet of conduit/conductors to the confirmed 240V Three phase service.Any help would be greatly appreciated. Thanks.

Possible Explanations



1. Transformer with Delta-Wye Configuration

It is possible that the transformer in the vault is configured as a delta-wye transformer. The delta side of the transformer would be connected to the single-phase, 7620V supply, while the wye side would provide three-phase, 240V power.

2. Phase-Splitting Capacitor

Another possibility is that the transformer vault contains a phase-splitting capacitor. This capacitor would split the single-phase supply into a balanced three-phase voltage using a capacitive reactance.

3. Rotary Phase Converter

A rotary phase converter can also be used to derive three-phase power from a single-phase supply. It consists of a motor and a capacitor bank that creates a rotating magnetic field, which induces three-phase voltages in the output windings.

Verification and Precautions

To determine the actual configuration, you should: Contact the utility company to gain access to the transformer vault. Use a multimeter or voltage tester to measure the voltage and current on the transformer terminals and the switchboard. If you observe a delta-wye configuration or phase-splitting capacitor, you can be certain that the system is providing three-phase power.

Safety Precautions:
7620V is an extremely high voltage and can be fatal. Only qualified electricians should perform any work on this system. Lock out the power source and ground the equipment before working on the transformer vault or switchboard. Flag for review