User: Michael15956, Location: NE Ohio

Asked on: Wednesday, March 2, 2011 at 7:05 pm EST
Answered on: Tuesday, May 14, 2024 at 2:17 am EDT

Question: Wound a bus bar connected to the exterior of a meter socket (for bonding intersystem grounding conductors) with self tapped screws and no bonding wire be a code violation? Our POCO allows this bar to be connected to the socket. Would this be considered "electrically" connected as required by 250.94(4)? I run the GEC to the rod(s) inside PVC Conduit for a cleaner look and I'm trying to avoid running another bonding wire to this bus bar. I use the Arlington Intersystem Bonding Bar for this application.

Code Violation

Yes, it would be a code violation to wind a bus bar connected to the exterior of a meter socket with self-tapped screws and no bonding wire. This method does not provide a reliable electrical connection.

Electrical Connection Required

According to 250.94(4) of the National Electrical Code (NEC), all intersystem grounding conductors (IGCs) must be "electrically connected" to the bonding bus bar. This means that the connection must be made using an approved method, such as: Bolting Clamping Welding Tinning and solderingSelf-tapped screws do not provide an adequate electrical connection because they can loosen over time, resulting in a potential hazard.

Bonding Wire Requirement

Yes, a bonding wire is required to connect the bonding bus bar to the grounding electrode conductor (GEC). The bonding wire must be sized according to Table 250.66 of the NEC.

Arlington Intersystem Bonding Bar

The Arlington Intersystem Bonding Bar is not approved for use with self-tapped screws. It must be installed using bolts or screws with nuts.

Recommended Practice:


The recommended practice is to install the intersystem grounding conductors using the following steps:1. Install the bonding bus bar on the exterior of the meter socket.
2. Attach the IGCs to the bonding bus bar using approved methods (bolting, clamping, etc.).3. Run a bonding wire from the bonding bus bar to the grounding electrode conductor (GEC).
4. Enclose the IGCs and bonding wire in PVC conduit for protection.This method will ensure a reliable electrical connection and compliance with the NEC. Flag for review