User: jusme123, Location: NY
Asked on: Wednesday, March 2, 2011 at 11:33 pm EST
Answered on: Tuesday, May 14, 2024 at 2:17 am EDT
Question: When terminating switch gear (bottom fed), is it permissible to take the grounds inside the conduits directly to the ground bus (bypassing grounding bushing), and than run one ground wire from the ground bus to all the grounding bushings on the conduits. Code section would be appreciated! Thanks
Yes, it is permissible to take the grounds inside the conduits directly to the ground bus (bypassing grounding bushing), and than run one ground wire from the ground bus to all the grounding bushings on the conduits.NEC Section 250.148(B): "The equipment grounding conductor shall be run with the circuit conductors inside the raceway, cable, or flexible cord, or otherwise run with or enclosed within the same raceway, cable, or flexible cord."NEC Section 250.70(A): "The grounding electrode conductor shall be connected to the grounding bus or to the grounding electrode system."NEC Section 250.104(A): "All metal raceways, cable trays, cable armor, and other metal enclosures for conductors shall be grounded."NEC Section 250.122(C): "Where raceways are used for grounding purposes, the connections between raceways and boxes, cabinets, and other equipment shall be made in accordance with 250.126."NEC Section 250.126(C): "Grounding bushings shall be used where conduits, nonmetallic raceways, or metal-clad cables enter ferrous metal boxes or cabinets."Exception: Where conductors enter through the side of the box or cabinet and the box or cabinet is grounded and secured to the metal raceway or cable armor by other means. Flag for review