User: wyreman, Location: SF CA USA
Asked on: Thursday, March 3, 2011 at 4:10 am EST
Answered on: Tuesday, May 14, 2024 at 2:17 am EDT
Question: What is the NEC code section that says you can't put a#14 jumper to a 15A device on a 20A ct.If the 15A device is allowed by exception on the 20A ct then so is the 15A pigtail. Not mixing wire sizes here downstream, just to the 15A device.Some 1990's installs I see all home runs in #12, cbs at 15A and then the lighting loops mixed down to #14, solid and better for voltage drop but no wire sizes/color changes allowed. The next guy might get confused. Forget about ring circuits at 120v, pressurized gas pipe hangers or the color scheme in Bahrain!:grin:
Section 210.19(A)(1) of the NEC states that "conductors of different sizes shall not be used in parallel unless the individual conductors have the same current-carrying capacity." Flag for review