User: Loffgren, Location: CA
Asked on: Thursday, March 3, 2011 at 10:37 am EST
Answered on: Tuesday, May 14, 2024 at 2:18 am EDT
Question: ok sorry dumb question, doing a residential load calc. The range in question name plate says 8.6kW and 11.6kw. my assumption is that those are for the top/bottom portions. Would the range be a "20.2kw" range?Thanks again
No, the range would not be a "20.2kW" range.The nameplate typically shows two power ratings: Element Rating
This is the total power consumption of all the heating elements in the range (both top and bottom). It is typically higher than the Connected Load because it includes inefficiencies in the heating elements and control circuits.
Connected Load
This is the maximum power consumption of the range when all heating elements and other electrical components (e.g., oven light, fan) are operating simultaneously. It is the value used for load calculations.In this case, the nameplate states that the range has an Element Rating of 8.6kW and a Connected Load of 11.6kW. Therefore, the Connected Load would be used for the load calculation, not the Element Rating.
So, the range would be an "11.6kW" range. Flag for review