Question: NEC Article 440.22 code interpretation question: An existing rooftop equipment is being replaced and is currently protected by 200A circuit breaker. new equipment has mca of 130, mocp of 175. Can the 200A circuit breaker be left and protect the #1/0 wiring with a fusible disconnect (200/175/3) at the rooftop unit? The 200A circuit breaker is still within 175% of the mca, but the unit has to be fused at 175. I guess my question is: with the addition of the fusible disconnect, are the wires from the panel now considered feeders and is normal wire sizing for 200A c/b (#3/0) applicable?
Interpretation
No, the 200A circuit breaker cannot be left to protect the #1/0 wiring with a 200/175/3 fusible disconnect at the rooftop unit.
Reasoning
NEC 440.22(A)(1) requires overcurrent protection at the point where the conductor enters the air-conditioning or refrigerating equipment. NEC 240.21(B)(1) requires overcurrent protection at the point where the feeder enters a building or other structure. The wiring from the panel to the fusible disconnect would be considered a feeder, since it supplies power to the equipment. The normal wire sizing for a 200A circuit breaker is indeed #3/0, as per NEC Table 310.16.
Conclusion:
To comply with the NEC, the following measures are required: Install a 175A circuit breaker at the panel to protect the #3/0 feeder. Install a 175A fusible disconnect at the rooftop unit to protect the #1/0 wiring entering the equipment. Flag for review