Topic: 240.80

User: ronmath, Location: Burnsville, MN

Asked on: Thursday, March 3, 2011 at 3:48 pm EST
Answered on: Tuesday, May 14, 2024 at 2:19 am EDT

Question: "Circuit breakers shall be trip free and capable of being closed and opened by manual operation"I am having an inspector telling me that we can not install lock-on devices on circuit breakers because of this statement (other than where specifically allowed elsewhere in the code as I pointed out). My interpretation would be that the devices can be easily removed and the breaker turned off manually. Any other opionions?Thanks,

The statement you provided from the code (NEC 240.85) requires that circuit breakers be "trip free" and capable of being "closed and opened by manual operation." This means that the circuit breaker must be able to trip open automatically in the event of a fault, and it must also be possible to manually turn the circuit breaker off and on.Lock-on devices can prevent the circuit breaker from being manually turned off. This means that it would not be possible to manually de-energize the circuit, which could create a safety hazard. For these reasons, lock-on devices are not permitted on circuit breakers, except in specific cases where they are specifically allowed by the code.In your case, the inspector is correct in telling you that you cannot install lock-on devices on circuit breakers. This is because lock-on devices would violate the requirement that circuit breakers be "trip free" and capable of being "closed and opened by manual operation." Flag for review