Topic: 392.56 Cable Splices. (2011)

User: cripple, Location: Santa Fe, New Mexico

Asked on: Thursday, March 3, 2011 at 4:10 pm EST
Answered on: Tuesday, May 14, 2024 at 2:19 am EDT

Question: Section 300.15 clearly requires a box or conduit body for all cable systems at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (L). All wiring methods in chapter 3 without a removable cover require a box or refer you back to 300.15. Section 90.3 states that the first 4 chapters apply generally and chapters 5, 6, and 7 supplement or modify the general rules.My question is why is it, that section 392.56 permit splicing of cables in cable tray without using box or conduit body. Section 392.56 has no reference to 110.14 or 300.15. I know that cable tray is not a wiring method and is defined as a structural system used to securely fasten or support cables and raceways systems. Since cable tray requirements are located in chapter 3 it should not modify the general rule or is there something I'm over looking or not grasping.

Section 110.3(B) of the National Electrical Code (NEC) states that "requirements specifically provided for individual materials, equipment, or construction methods shall take precedence over general requirements." In other words, if there is a specific rule that applies to a particular situation, that rule takes precedence over the general rule.
392.56 is a specific rule that applies to splicing of cables in cable tray. It states that "Splices made in cable tray shall be accessible and shall be made in a listed splicing device or by methods that provide equivalent protection to that afforded by a listed splicing device." This rule does not require the use of a box or conduit body, but it does require that the splice be made in a listed splicing device or by a method that provides equivalent protection.Therefore, 392.56 takes precedence over 300.15 for splices made in cable tray. This is because 392.56 is a specific rule that applies to cable tray, and it does not require the use of a box or conduit body. Flag for review

Previous Question Next Question