Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Residential 2 hour rated fire wall

User: bkelly, Location: NE Arkansas

Asked on: Thursday, March 3, 2011 at 4:59 pm EST
Answered on: Tuesday, May 14, 2024 at 2:19 am EDT

Question: What are the requirements or limitations for nm cable and plastic boxes in a residential 2 hour rated firewall in townhomes. From what I can understand, a 2 hour rated, load bearing wood stud wall between the townhomes, woiuld require conduit for the nm cable. Any one have any info on this?

Requirements for NM Cable and Plastic Boxes in 2 Hour Rated Firewalls in TownhomesNEC Code Requirements



NEC 334.15(B)

NM cable shall not be installed in a rated fire-resistant wall.


NEC 314.17(C)

In 2-hour fire-rated walls, all electrical circuits shall be installed in approved raceways (e.g., conduit).

Exceptions



NEC 334.15(B) Exception

NM cable is allowed in 2-hour rated firewalls provided it is installed in accordance with the following requirements:
The NM cable is contained within a metal raceway or sleeve extending through the firewall. The raceway or sleeve is securely fastened to the firewall and sealed with an approved firestop system.

NEC 314.17(C) Exception

Electrical circuits in 2-hour rated firewalls may be installed without raceways if they are: "Listed as a fire-resistant assembly" or "Installed using approved methods to maintain the fire-resistance rating of the wall."

Plastic Boxes

Plastic electrical boxes are generally not approved for use in 2-hour rated firewalls. However, some plastic boxes may be listed for use in fire-resistant walls when used in conjunction with approved fire-resistant inserts or barriers.

Recommendations:


For electrical installations in townhomes with 2-hour rated firewall walls, it is strongly recommended to follow the standard NEC requirements and install NM cable in approved raceways and use metal electrical boxes in both fire-rated and non-fire-rated areas.To ensure compliance and safety, it is advisable to consult with a licensed electrician or local building code authority for specific requirements and guidance. Flag for review

Previous Question Next Question