User: bs1224, Location: Massachusetts
Asked on: Thursday, March 3, 2011 at 6:14 pm EST
Answered on: Tuesday, May 14, 2024 at 2:19 am EDT
Question: I am installing a fire alarm system and have finished running the wire and devicing. I am wondering what i should be reading for when i test between both the supply and return. I have no shorts to ground, but i read resistance between the conductors.
Resistance Readings for Fire Alarm System WiringSupply and Return Conductors
Normal Reading
Open circuit (infinite resistance)
Reading Indicates a Problem
Resistance value lower than infinite, indicating a short circuit or partial short circuit.
Possible Causes of Resistance Readings Between Supply and Return Conductors
Shorts
Direct contact between the supply and return conductors or their insulation.
Partial Shorts
Insulation damage or degradation that allows current to leak between conductors.
Capacitance
In long cable runs, capacitance can create a small amount of resistance between conductors. This is typically not a problem unless it exceeds certain limits.
Check for Capacitance
Disconnect the wire from the fire alarm panel and measure the resistance between the supply and return conductors. If the resistance reading remains, then it is likely due to capacitance. If the resistance reading drops to infinite after disconnecting, then it is likely a short circuit.
Acceptable Capacitance Values
Capacitance should not exceed 250 nanofarads (nF) per 1,000 feet of cable. For example, a 5,000-foot cable should have a maximum capacitance of 1,250 nF.
Troubleshooting: If you read resistance between the supply and return conductors, troubleshoot the wiring for potential shorts or partial shorts. Inspect the wire for any damage or insulation issues. Check if the wire is properly secured and not subject to excessive vibration or movement. Disconnect any devices connected to the wire and test again to isolate the problem. Flag for review