Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Telephone wire supports

User: [email protected], Location: Plant city,fl

Asked on: Friday, March 4, 2011 at 2:31 pm EST
Answered on: Tuesday, May 14, 2024 at 2:21 am EDT

Question: What is the rule on telephone wire support that not encased? I looked in the NEC 08 and read though the 800's and all i could find is,the building can support the wire, anyway as long as the wire can't be damaged by use's of the building.Can anyone help me in this matter?I have to get a low voltage permit but there's no direction in the installation?Other than wire size and type's of low voltage circuit's.Thank you,Stafford Electric

NEC 2008 Section 800.35(C) Telephone Circuit Conductors Not Encased Conductors shall be supported on insulators at intervals not exceeding 250 feet and at the termination of the run.* Conductors shall be separated at least 4 inches (102 mm) from other conductors or surfaces, except for short jumpers between buildings. Flag for review

Previous Question Next Question