Question: Isn't 110.14 C in direct conflict with 110.14 (1) (a)2 and 3In other words let's say I'm using #12 THHN 90 degree wire (dry location) 6 curent carrying conductors in a 3/4" raceway.The way I read 110.14 c is that I can use the 90 degree column 310.16 for ampacity adjustment, which after derating per 310.15 b 2 a The ampacity of the wire would be 24ampHowever when I read on 110.14 (1) (a)2 and 3 This tell me either use 60 degree column or 75 degree if the termination is rated as such. Now doing the same calculation above but using 75 degree column I'm at 20amp.What am I missing one says I can use 90 degree column and the other tells me i can not.
You are correct in your interpretation of the conflict between Section 110.14(C) and Section 110.14(1)(a)2 and 3 of the National Electrical Code (NEC).
Section 110.14(C) permits the use of the 90°C column values from Table 310.16 for ampacity adjustment of conductors in raceways where the temperature is not likely to exceed 30°C.
Section 110.14(1)(a)2 and 3 requires the use of the 60°C or 75°C column values for ampacity adjustment if the conductor terminations are rated at those temperatures.In your example, the wire used is THHN, which has a 90°C temperature rating. Therefore, according to Section 110.14(C), you could use the 90°C column values for ampacity adjustment. However, since the termination temperature is not specified, Section 110.14(1)(a)2 and 3 requires you to use the 75°C column values.
To resolve this conflict, you must use the 75°C column values for ampacity adjustment.
Therefore, for 6 current-carrying conductors in a 3/4" raceway using #12 THHN wire in a dry location, the ampacity would be 20 amps as calculated using the 75°C column. Flag for review